Water cooling requirements
Follow these requirements when using water cooling for the 9125-F2A.
Determining minimum required system flow and pressure
Determining minimum required system flow and pressure for a normal operating system
  1. Determine the inlet water temperature. This is the temperature of the chilled water that is present in the room where the system is installed.
  2. Determine the minimum design flow rate for your rack configuration using tables Required building chilled water flow, pressure drop and Required building chilled water flow, pressure drop and outlet temperature (English units). Under normal operating conditions the flow into the frame will be double that of the numbers shown in the tables. This is because both Water Conditioning Units (WCU) in the frame operate simultaneously.
    Note: If there is a possibility that you will add nodes to a partially populated system at a later date, you should plan for it during the initial installation.
  3. Determine the minimum pressure required across the ends of the hoses to provide the flow rate determined in the step above. Maximum continuous operating pressure must not exceed 2.32 bars (33.7 psi).
Determining additional required system flow for a fault condition
Define the maximum facility pressure drop that can be present across the ends of the model 9125-F2A hoses, and locate the equivalent pressure drop in tables Required building chilled water flow, pressure drop and Required building chilled water flow, pressure drop and outlet temperature (English units). The corresponding flow rate multiplied by two represents the maximum flow a single rack could experience under a worst-case fault condition. The facility must be able to accommodate this condition for at least one 9125-F2A racks in the installation.
Table 1. Required building chilled water flow, pressure drop °C (1 of 2)
Nodes Cooling capacity with two active WCUs Required Chilled Water per WCU 6 7 8 9 10
2 4.9 Flow (lpm) 3.7 4 4.4 4.9 5.5
Pressure Drop (Bar) 0.34 0.34 0.34 0.34 0.34
Outlet temperature °C 25.1 24.4 23.8 23.2 22.7
4 9.7 Flow (lpm) 8.4 9.1 9.9 10.8 11.9
Outlet temperature °C 22.7 22.4 22.2 22.0 21.8
6 14.6 Flow (lpm) 13 14 15.1 16.5 18.1
Outlet temperature °C 22.2 22.0 21.8 21.7 21.6
8 19.5 Flow (lpm) 17.5 18.9 20.5 22.3 24.5
Outlet temperature °C 21.9 21.8 21.7 21.5 21.4
10 24.4 Flow (lpm) 22.2 23.9 25.9 28.3 31.2
Pressure Drop (Bar) 0.34 0.34 0.34 0.34 0.39
Outlet temperature °C 21.8 21.6 21.5 21.4 21.2
12 29.2 Flow (lpm) 26.9 29 31.5 34.6 38.4
Pressure Drop (Bar) 0.34 0.34 0.4 0.47 0.58
Outlet temperature °C 21.6 21.5 21.3 21.1 20.9
14 34.1 Flow (lpm) 31.7 34.4 37.5 41.3 46.2
Pressure Drop (Bar) 0.4 0.47 0.55 0.67 0.82
Outlet temperature °C 21.4 21.2 21.1 20.8 20.6
Table 2. Required building chilled water flow, pressure drop °C (2 of 2)
Nodes Cooling capacity with two active WCUs Required Chilled Water per WCU 11 12 13 14 15 16
2 4.9 Flow (lpm) 6.2 7 8.1 9.6 11.5 14.4
Pressure Drop (Bar) 0.34 0.34 0.34 0.34 0.34 0.34
Outlet temperature °C 22.3 21.9 21.6 21.3 21.1 20.9
4 9.7 Flow (lpm) 13.2 14.8 16.9 19.7 23.6 29.5
Pressure Drop (Bar) 0.34 0.34 0.34 0.34 0.34 0.35
Outlet temperature °C 21.6 21.4 21.3 21.1 20.9 20.7
6 14.6 Flow (lpm) 20.1 22.6 25.9 30.3 36.8 47.8
Pressure Drop (Bar) 0.34 0.34 0.34 0.37 0.53 0.88
Outlet temperature °C 21.4 21.3 21.1 20.9 20.7 20.4
8 19.5 Flow (lpm) 27.3 30.8 35.5 42.2 53.1 77.8
Pressure Drop (Bar) 0.34 0.38 0.5 0.69 1.08 2.23
Outlet temperature °C 21.2 21.1 20.9 20.6 20.3 19.6
10 24.4 Flow (lpm) 34.9 39.8 46.5 57.1 78.5
Pressure Drop (Bar) 0.48 0.62 0.83 1.23 2.27
Outlet temperature °C 21.0 20.8 20.5 20.1 19.5
12 29.2 Flow (lpm) 43.3 50 60.1 79
Pressure Drop (Bar) 0.73 0.96 1.36 2.3
Outlet temperature °C 20.7 20.4 20.0 19.3
14 34.1 Flow (lpm) 52.8 62.5 79.4
Pressure Drop (Bar) 1.06 1.47 2.32
Outlet temperature °C 20.3 19.8 19.2
Table 3. Required building chilled water flow, pressure drop and outlet temperature (English units) °F (1 of 2)
Nodes Cooling capacity with two active WCUs Required Chilled Water per WCU 42.8 44.6 46.4 48.2 50.0 51.8
2 16.6 Flow (gpm) 1 1.1 1.2 1.3 1.5 1.6
Pressure Drop (psid) 5 5 5 5 5 5
Outlet temperature °F 77.1 75.9 74.8 73.8 72.9 72.1
4 33.3 Flow (gpm) 2.2 2.4 2.6 2.8 3.1 3.5
Outlet temperature °F 72.8 72.3 71.9 71.6 71.2 70.9
6 49.9 Flow (gpm) 3.4 3.7 4 4.4 4.8 5.3
Outlet temperature °F 71.9 71.6 71.3 71.1 70.8 70.5
8 66.6 Flow (gpm) 4.6 5 5.4 5.9 6.5 7.2
Outlet temperature °F 71.5 71.3 71.0 70.8 70.5 70.2
10 83.2 Flow (gpm) 5.9 6.3 6.8 7.5 8.2 9.2
Pressure Drop (psid) 5 5 5 5 5.6 7
Outlet temperature °F 71.2 71.0 70.7 70.4 70.2 69.8
12 99.9 Flow (gpm) 7.1 7.7 8.3 9.1 10.1 11.4
Pressure Drop (psid) 5 5 5.7 6.9 8.4 10.5
Outlet temperature °F 70.9 70.6 70.4 70.0 69.7 69.2
14 116.5 Flow (gpm) 8.4 9.1 9.9 10.9 12.2 14
Pressure Drop (psid) 5.8 6.8 8 9.6 12 15.4
Outlet temperature °F 70.6 70.2 69.9 69.5 69.1 68.5
Table 4. Required building chilled water flow, pressure drop and outlet temperature (English units) °F (2 of 2)
Nodes Cooling capacity with two active WCUs Required Chilled Water per WCU 53.6 55.4 57.2 59.0 60.8
2 16.6 Flow (gpm) 1.9 2.1 2.5 3 3.8
Outlet temperature °F 71.5 70.9 70.4 69.9 69.6
4 33.3 Flow (gpm) 3.9 4.5 5.2 6.2 7.8
Pressure Drop (psid) 5 5 5 5 5.1
Outlet temperature °F 70.6 70.3 70.0 69.7 69.3
6 49.9 Flow (gpm) 6 6.8 8 9.7 12.6
Pressure Drop (psid) 5 5 5.3 7.7 12.8
Outlet temperature °F 70.3 70.0 69.7 69.3 68.7
8 66.6 Flow (gpm) 8.1 9.4 11.2 14 20.5
Pressure Drop (psid) 5.5 7.2 10.1 15.6 32.4
Outlet temperature °F 69.9 69.6 69.1 68.5 67.3
10 83.2 Flow (gpm) 10.5 12.3 15.1 20.7
Pressure Drop (psid) 9 12.1 17.9 32.9
Outlet temperature °F 69.4 68.9 68.2 67.0
12 99.9 Flow (gpm) 13.2 15.9 20.9
Pressure Drop (psid) 13.9 19.8 33.3
Outlet temperature °F 68.7 68.0 66.8
14 116.5 Flow (gpm) 16.5 21
Pressure Drop (psid) 21.3 33.7
Outlet temperature °F 67.7 66.5
Figure 1. Pressure versus flow with a 427 cm (14 ft) hose – International System of Units (SI units)
Pressure versus Flow with 427 cm (14 ft) Hose – SI Units
Figure 2. Pressure versus flow with a 427 cm (14 ft ) hose – English units
Pressure versus Flow with 427 cm (14 ft) Hose – English units
Note: Curves are with MWU inlet valve in the fully opened position. The customer pressure-versus-flow behavior of the system will not match this curve under normal operating conditions because the valve position adjusts to regulate the flow to maintain a fixed system-side water temperature.
Principal of operation
Figure 3. Simplified schematic of water cooling system
Calculating building chilled water return temperature (SI units)
Treturn (°C) = Tsupply (°C)+ 14.4 (Q (MWU (kW)/ (MWU BCW Flow (lpm))
Return water temperature can be calculated under normal operating conditions using the previous table, Required Building Chilled Water Flow per MWU (lpm).
Examples in SI units
Tsupply(°C) = 10. That is, the facilities water is 10 °C.
Frame Heat Load(kw) = 34.1. T he heat load to water in kilowatts of the system is 34.1 kW.
Frame BCW Flow(gpm) = 44.9. The flow of the facilities water is 44.9 liters per minute.
Treturn = 10+ 14.4 (34.1/44.9) = 20.9 °C
Calculating building chilled water return temperature (English units)
Treturn (°F) = Tsupply (F) + 2.0 (QMWU (kBTU/hr) / (MWU BCW Flow (gpm))
Return water temperature can be calculated under normal operating conditions using the Required Building Chilled Water Flow per MWU (gpm) table.
Examples in English units
Tsupply(°F) = 50. That is, the facilities water is 50 °F.
Frame Heat Load(kw) = 116.5 The heat load to water in Kilo British Thermal Units (kBTU) per hour of the system is 116.5 kBTU per hour.
Frame BCW Flow(gpm) = 11.9. The flow of the facilities water is 11.9 gallons per minute.
Treturn = 50+2.0 (116.5/11.9) = 69.6 °F
Facility water momentary flow interruption and out of specification temperature
The system is designed to tolerate a momentary interruption of facility water flow or temperature increase that might occur as a result of a failure in the facility water distribution system.
Momentary interruption of facility water flow
The system can tolerate complete loss of facilities water flow for 60 seconds. There is a high probability that nodes will be powered off by thermal protection circuits internal to the 9125-F2A if loss of flow exceeds this time.
Over-temperature of facility water
The system can tolerate a 14°C (26°F temperature rise above the maximum facilities operating temperature at a given flow rate. It should be assumed that the system will be powered off by the thermal protection circuits internal to the 9125-F2A for facility water temperatures greater than this maximum temperature rise. Continuous operation in an over-temperature condition of 1 - 14°C (2 - 25°F) cannot be sustained, even though the system will run without powering down. When the maximum allowable facility water temperature of 16°C (60.8°F) is exceeded, or when the system-side water temperature cannot be regulated, an error is sent to the customer, and corrective action is required.
Under-temperature facility water
If facility water is below the minimum allowable temperature of 4.4 °C (40 °F) an error will be surfaced to the customer and corrective action will be required. The only problem that can result from under-temperature facility water is condensation on the facility side of the system. The temperature at which condensation might occur is dependant on the severity of the facility water under-temperature and the air temperature and humidity in the room.
Facility water quality and fowling
In general the 9125-F2A requires standard building chilled water temperatures without any special requirements.
Note: The facility water flows only through the facility side of the water-to-water heat exchanges located in the bottom rear of the rack. Therefore, contaminated facility water cannot damage components within the rack other than the WCUs.
The quality of the facilities water is as follows.
Note: Facility water should be tested by qualified personnel to determine whether it meets these requirements.
Deionized water with benzotriazole solution installation and maintenance
IBM is responsible for supplying and maintaining the internal frame secondary loop side water. This protects the system processor books and distribution plumbing from damage that could result from the use of contaminated water.
IBM supplies a water solution that is mixed with benzotriazole (BTA), a corrosion inhibitor, for the internal secondary cooling loop of the frame when it is installed and when any repairs are performed that require water to be added.
IBM uses certified suppliers for the water solution that satisfy all pertinent environmental control requirements.
Deionized water with benzotriazole disposal
The customer must dispose of the water solution in accordance with applicable laws and regulations and product characteristics at the time of disposal.
Internal frame water solutions
IBM will supply the system-side water.
Water and benzotriazole solution
Benzotriazole (BTA) is mixed with the deionized (DI) water to a concentration of 1000 parts per million by weight.
Deionized water
The deionized water used in IBM water cooling systems conforms to type II, grade A specifications in ASTM D1193-06 entitled, standard specifications for reagent water. Specifications are as follows:
Benzotriazole
Benzotriazole (BTA) is purchased from Sigma-Aldrich or an alternative IBM approved supplier, and is defined as follows:
Connection of facility water to the system
Two pairs of insulated 25.4 mm (1 in.) inside diameter (38.4 mm outside diameter / 1.51 in.) hoses, which are specified by IBM, connect facility water to the system. The hoses are available in 1.83 m (6 ft) and 4.27 m (14 ft) lengths, and can be purchased from IBM or purchased directly from the hose assembly manufacturer using a part number. The hoses must be attached to the facility water source, and the system ends must be properly positioned above the raised floor prior to the server arriving so that the rack can be rolled into positions, up to the hoses, without delay.
Installation of IBM system connection hoses in facility
The following figure shows the four hoses (two supply hoses and two return hoses) connected to the building water manifolds under the raised floor with the ends that connect to the system properly positioned 188 mm (7.4 in.) above the floor.
The facility end of the provided hoses is a cut hose without a fitting. It is the customer's responsibility to determine the connection technique on this side.
It is suggested, but not required, that a shutoff valve be provided in front of the hose assembly as shown. This shutoff valve is not required for maintenance of the equipment, but can be useful if hose removal is ever desired by the customer.
The 1.83 m (6 ft) and 4.27 m (14 ft) hose length is the customer's responsibility and depends on the distance from the facility manifolds to the rack. The facility end of the hose can be cut to the desired length by the hose installer.
Route the hoses through the floor cutout as shown, being sure to avoid sharp edges of metal and to leave some slack in the hose. Cable management is required for signal cables that exit the rear of the rack and must be considered when routing the hoses. In the proceeding figure the cable management tray is provided as part of the facility at the rear of the rack.
IBM hose assembly ordering information
Four hoses (two supply and two return) and one hose positioning fixture is required for each rack that will be installed. The hose positioning fixture is removed after the hoses are connected to the system.
Ordered hose kits from IBM arrive with the system. However, it is recommended that you order the hose kits before the system, so that they can be attached to the facilities plumbing in advance. The hose kits must be ordered directly from the hose kit manufacturer.
Hose assembly ordering information
Two supply hoses, two return hoses, and one hose positioning fixture are required for each rack to be installed.
Note: The hose positioning fixture is removed after the hoses are connected to the system.
In order for the hose kits to arrive before the system, the hose kits must be ordered from IBM by ordering the 9125-F2A Site Preparation/Install Support Model 9125-F2B. The 9125-F2A Site Preparation/Install Support Model (9125-F2B) enables the ability to place an order for the Coolant Supply/Return Hoses (#6876 or #6877) prior to delivery of the system. This allows the site chilled water plumbing to be completed ahead of the system arrival, so the hose kits can be attached to facilities plumbing in advance, reducing overall installation time. Order either of the following if hoses are required before the systems.
If it is not necessary to receive the hose kits prior to installation, then you can order the following hose kits:
Figure 4. View of properly positioned facilities hoses
Figure 5. Facility water quick disconnects at rear base of frame
Figure 6. 9125-F2A water hook up locations
Hose materials
Only IBM hoses can be used to connect to the IBM 9125-F2A server. This protects against leaks and condensation that can result from using insufficient hose assemblies and incompatible quick disconnect couplings.
The hose contains the following components:
Figure 7. Facilities connection hose
Quick disconnect couplings insulator information
The quick disconnect coupling insulators shown in the following figure, are shipped with the system.
Figure 8. Quick disconnect coupling insulator open and closed
The quick disconnect couplings insulators must be attached as shown in Quick disconnect couplings without insulator (left) and with insulator (right) or condensation might occur on the quick disconnect.
Figure 9. Quick disconnect coupling without insulator (left) and with insulator (right)
Quick disconnect coupling with out insulator (left) and with insulator (right)
Purging air from facilities-side hoses
It is recommended that you purge the air from the facilities connection hoses when the contractor installs the hoses.
The hoses can contain a maximum of 0.51 liters per meter (0.041 gallons per foot) of air.
A hose purge operation is not done when the system is connected to the hoses because it is assumed that purging the hoses is completed by the hose installation contractor if it is thought to be necessary in the facility. The suggested procedure to purge air from the hoses during installation is as follows.
Figure 10. Purge drawing
Purge drawing
Figure 11. Facilities water quick disconnects (disengaged with both valves opened)
Facilities water quick disconnects (disengaged with both valves opnened)
Figure 12. Facilities water quick disconnects (mated with one valve opened)
Figure 13. Facilities water quick disconnects (mated with both valves opened)
  1. After final connection of the hoses to the facility supply and return is made, connect the supply quick disconnect coupling to the return quick disconnect coupling as shown in the preceding figure.
  2. After the connectors are twisted together, open the valve handle on one of the two connectors to lock the quick disconnects together.
  3. Slowly open the valve on the other connector, allowing the air trapped in the hoses to be moved slowly into the return side of the facility. Slowly removing the air prevents a large amount of air from entering the return all at once and allows the air to find its way to the facility's high point vent.
  4. After purging is complete, disconnect the quick disconnects from one another and place them in their proper locations in the positioning fixture above the raised floor, in preparation for rack installation.
Note: Knowledge of how the water cooling system works is beneficial to the mechanical engineering firm, mechanical contracting firm, the plumbing firm, and the customer.
Last updated: Tue, June 17, 2014