IBM Support
Setting QUPS* System Values and Power Handling Programs
Troubleshooting
Problem
How can I set up UPS power handling CL programs?
Resolving The Problem
Set the system value related to UPS using the WRKSYSVAL QUPS* command, and select Option 2 on QUPSDLYTIM and QUSRMSGQ. In QUPSDLYTIME, specify the delay time to reflect the time the UPS batteries can keep your system up and running minus the time it takes for an orderly shutdown of the system. Be conservative with this value. In QUPSMSGQ, specify the message queue to send messages; for example, CPF1816 indicating that utility power has failed.
The following are excerpts from the Backup and Recovery guide to help write, set up, and test a CL power handling program.
Example Power Handling CL Program
You can use the sample program with a full uninterruptible power supply. Although this sample CL program will work correctly as written, you should tailor it to your specific system requirements. For example, add additional recovery to the program by monitoring for error conditions specific to your system. You will also need to supply a user-written program that performs the steps necessary to prepare for a normal shutdown of the system. These steps may include holding job queues, sending messages, and ending subsystems. The program should restart normal operations should the power outage end before the system is powered down. The program performs the following:
1. The power-handling program retrieves the system value QUPSMSGQ into the variables &LIB and &MSGQ. Although this is not necessary, it helps ensure that the correct message queue is allocated each time the program is started. The program then deletes the message queue (if it already exists) and then creates it again. This step helps eliminate clearing the message queue or any problems that might occur if the message queue is damaged.
2. After the message queue is created, the program must allocate (ALCOBJ command) the message queue exclusively. Note: When the system value QUPSDLYTIM is set to *NOMAX, use one of the following methods to allocate the message queue that is specified for system value QUPSMSGQ:
-- Use the command CHGMSGQ MSGQ(QUPSLIB/QUPSMSGQ) MODE(*BREAK)
-- Include the ALCOBJ command within the power-handling program
Use only one of the methods that are listed. When a change in power activates the UPS, this message queue receives the UPS activated message (CPF1816). If the system value QUPSDLYTIM is *NOMAX, the following conditions must be met or the system will begin an immediate power down.
o The message queue specified in the QUPSMSGQ system value must exist.
o If the message queue is a work station message queue (or QSYSOPR), it must be in break or notify mode.
o If the message queue is not a work station message queue, it must be allocated by a job.
Note: If a power handling hangs or fails to function, the system will react according to the QUPSDLYTIM setting.
3. At Label A in the example power handling program, the Receive Message (RCVMSG) command is used to determine what message has been sent to the message queue. The RCVMSG command is also used to determine the amount of wait time (WAIT parameter) throughout the program. On line 27.00 of the example power-handling program, the value of the WAIT parameter on the RCVMSG command causes the program to wait 600 seconds (ten minutes). After ten minutes, the program checks to see if a controlled end to the job occurred (using the ENDSBS or ENDJOB command). This prevents the never-ending program from delaying the ENDJOB or ENDSBS command. If you use ENDSBS *IMMED or ENDJOB *IMMED, this part of the program can be removed. You can change the value for the WAIT parameter on the RCVMSG command to *MAX. The RCVMSG command runs immediately if the system sends a message to the message queue that is specified on the RCVMSG command. This occurs regardless of the value that is specified for the WAIT parameter.
4. If the message that is received by the RCVMSG command is CPF1816 (system utility power failed), the program checks to see if this is simply a short power failure. The program runs a second RCVMSG command with a value of ten seconds for the WAIT parameter (you must decide how many seconds is adequate for your site). If the message that is received by the RCVMSG command within the specified ten seconds is CPF1817 (system utility power restored), power was restored. The program returns to Label A and starts the cycle again.
If the 10-second limit is reached and no message is received, the power failure is longer than ten seconds and additional steps are necessary. At this point, you can call a user-written program that performs the following actions:
-- The program uses the HLDJOBQ command to hold certain long running batch jobs.
-- The program notifies unaffected remote users.
-- The program begins ending jobs and subsystems in an orderly manner.
5. At Label B in the example power-handling program, the program attempts to wait-out the power failure. The program retrieves the present time and places this information into a CL variable named &START. The present time is used to determine how much uninterruptible power supply time is remaining. A third RCVMSG command runs, and a CL variable named &WAIT (that was changed earlier in the program) determines the value for the WAIT parameter. The CL variable &WAIT is the amount of reserve power the uninterruptible power supply can provide. The value for the &WAIT variable at Label A should be adjusted to the amount of reserve power that the uninterruptible power supply can provide. (The amount of reserve power is measured in seconds.)
In the example program, the value of the &WAIT variable is set to 1200 seconds (20 minutes). If message CPF1817 (System utility power restored) is received during that time, power has been restored, and another program can be called to restart normal system operations. The program then returns to Label A and starts the cycle again. If message CPF1817 is not sent after 1200 seconds, the RCVMSG command returns a blank message ID (not equal to CPF1817). This indicates that power has not been restored, and an immediate system power down is started. If a message other than CPF1817 is received during this 1200-second wait, the following actions occur:
-- The program retrieves the present time and calculates how much of the 1200-second wait period has elapsed.
-- The program subtracts the difference, and changes the CL variable &WAIT to reflect that amount.
-- The program returns to label B to use the remaining power that is provided by the uninterruptible power supply.
This part of the program checks to see if a date change occurs which is necessary if the power outage occur on a different date.
Note: This program is provided as-is and any questions regarding the program are not supported under a standard SWMA contract.
SEQNBR*...+... 1 ...+... 2 ...+... 3 ...+... 4 ...+... 5 ...+... 6 ...
     1.00        PGM
     2.00        DCL      VAR(&UPSMSGQ)  TYPE(*CHAR)  LEN(20)
     3.00        DCL      VAR(&LIB)      TYPE(*CHAR)  LEN(20)
     4.00        DCL      VAR(&MSGQ)     TYPE(*CHAR)  LEN(20)
     5.00        DCL      VAR(&MSGID)    TYPE(*CHAR)  LEN(7)
     6.00        DCL      VAR(&ENDSTS)   TYPE(*CHAR)  LEN(1)
     7.00        DCL      VAR(&WAIT)     TYPE(*DEC)   LEN(6)
     8.00        DCL      VAR(&HOUR)     TYPE(*DEC)   LEN(6)
     9.00        DCL      VAR(&MIN)      TYPE(*DEC)   LEN(6)
    10.00        DCL      VAR(&SEC)      TYPE(*DEC)   LEN(6)
    11.00        DCL      VAR(&TIME)     TYPE(*CHAR)  LEN(6)
     12.00        DCL      VAR(&START)    TYPE(*DEC)   LEN(6)
    13.00        DCL      VAR(&END)      TYPE(*DEC)   LEN(6)
    14.00        DCL      VAR(&RESULT)   TYPE(*DEC)   LEN(6)
    15.00
    16.00        RTVSYSVAL  SYSVAL(QUPSMSGQ) RTNVAR(&UPSMSGQ)
    17.00        CHGVAR     VAR(&MSGQ) VALUE(%SST(&UPSMSGQ 1 10))
    18.00        CHGVAR     VAR(&LIB)  VALUE(%SST(&UPSMSGQ 11 10))
    19.00        DLTMSGQ    MSGQ(&LIB/&MSGQ)
    20.00        MONMSG     MSGID(CPF2105) /* Message queue not found. */
    21.00        CRTMSGQ    MSGQ(&LIB/&MSGQ) TEXT('UPS Power handling +
    22.00                          program message queue') AUT(*EXCLUDE)
     23.00        CHGMSGQ    MSGQ(&LIB/&MSGQ) DLVRY(*HOLD)
    24.00        ALCOBJ     OBJ((&LIB/&MSGQ *MSGQ *EXCL))
    25.00
    26.00  A:    RCVMSG     MSGQ(&LIB/&MSGQ) WAIT(600) RMV(*YES) +
    27.00                          MSGID(&MSGID)
    28.00        IF         COND(&MSGID *NE CPF1816) THEN(DO)
    29.00        RTVJOBA    ENDSTS(&ENDSTS)
    30.00        IF         COND(&ENDSTS *EQ '1') THEN(GOTO CMDLBL(ENDPGM))
    31.00        GOTO       CMDLBL(A)
    32.00        ENDDO
    33.00
    34.00       /* Check to see if this is a short power outage. */
    35.00       IF         COND(&MSGID *EQ CPF1816) THEN(DO)
    36.00       RCVMSG     MSGQ(&LIB/&MSGQ); WAIT(10) RMV(*YES) +
    37.00                     MSGID(&MSGID); /* Wait ten seconds)
    38.00       IF         COND(&MSGID *EQ CPF1817) THEN(GOTO CMDLBL(A))
    39.00       ENDDO
    40.00
    41.00       /* Power outage was longer than 10 seconds.  */
     42.00       CALL       PGM(LIB/PGM) /* User program that prepares +
    43.00                          system for possible shutdown. */
    44.00
    45.00      /* Check to see if this is a long power outage. */
    46.00       CHGVAR     VAR(&WAIT); VALUE(01200) /* 20 minutes. */
    47.00  B:   RTVSYSVAL  SYSVAL(QTIME) RTNVAR(&TIME);
    48.00       CHGVAR     VAR(&HOUR);  VALUE(%SST(&TIME 1 2))
    49.00       CHGVAR     VAR(&MIN);   VALUE(%SST(&TIME 3 2))
    50.00       CHGVAR     VAR(&SEC);   VALUE(%SST(&TIME 5 2))
    51.00       CHGVAR     VAR(&START); VALUE((&SEC); + (&MIN * 60) + +
    52.00                     (&HOUR * 3600))
    53.00       RCVMSG     MSGQ(&LIB/&MSGQ); WAIT(&WAIT); RMV(*YES) +
    54.00                          MSGID(&MSGID);
    55.00       IF         COND(&MSGID *EQ CPF1817) THEN(DO)
    56.00       CALL       PGM(LIB/PGM) /* User program that restarts +
    57.00                     system operations. */
    58.00       GOTO       CMDLBL(A)
    59.00       ENDDO
    60.00
    61.00       IF         COND(&MSGID *NE CPF1817) THEN(DO)
    62.00       RTVSYSVAL  SYSVAL(QTIME) RTNVAR(&TIME)
    63.00       CHGVAR     VAR(&HOUR)  VALUE(%SST(&TIME 1 2))
    64.00       CHGVAR     VAR(&MIN)   VALUE(%SST(&TIME 3 2))
    65.00       CHGVAR     VAR(&SEC)   VALUE(%SST(&TIME 5 2))
    66.00       CHGVAR     VAR(&END)   VALUE((&SEC) + (&MIN * 60) + +
     67.00                   (&HOUR * 3600))
    68.00       CHGVAR     VAR(&RESULT); VALUE(&END - &START)
    69.00       IF         COND(&RESULT < 0) THEN(CHGVAR VAR(&RESULT) +
    70.00                     VALUE(86400 + &RESULT)) /* Check for +
    71.00                          change of day.  86400 = 24 hours. */
    72.00       IF         COND(&RESULT *GE &WAIT) THEN(PWRDWNSYS +
    73.00                   OPTION(*IMMED) /* UPS battery reserve has +
    74.00                    expired. */
    75.00       CHGVAR     VAR(&WAIT) VALUE(&WAIT - &RESULT) /* UPS +
    76.00                          battery reserve has not expired. */
    77.00       GOTO       CMDLBL(B)
    78.00       ENDDO
    79.00
    80.00  ENDPGM:    DLCOBJ     OBJ((&LIB/&MSGQ *MSGQ *EXCL))
    81.00             ENDPGM
Power Failure Handling - IBM i in a Hosted Environment
For information regarding power failure handling information in IBM i hosted environments, refer to the following document - Power Failure Handling - IBM i in a Hosted Environment :
http://www-01.ibm.com/support/docview.wss?uid=nas8N1011322
[{"Type":"MASTER","Line of Business":{"code":"LOB57","label":"Power"},"Business Unit":{"code":"BU058","label":"IBM Infrastructure w\/TPS"},"Product":{"code":"SWG60","label":"IBM i"},"ARM Category":[{"code":"a8m0z0000000CGbAAM","label":"General Information"}],"ARM Case Number":"","Platform":[{"code":"PF012","label":"IBM i"}],"Version":"All Versions"}]