None, but the system-error LED is
lit. |
An error has occurred and cannot be diagnosed,
or the IMM has failed. The error is not represented by a light path
diagnostics LED. |
Use the Setup utility to check the system-event
log for information about the error.
|
BRD |
An error has occurred on the system board. |
- Check the LEDs on the system board to identify the component that
is causing the error. The BRD LED can be lit for the following conditions:
- Battery
- Missing PCI riser-card assembly
- Failed voltage regulator
- Check the system-event log for information about the error.
- Replace any failed or missing replaceable components, such as
the battery (see Removing the battery for more
information) or PCI riser-card assembly (see Removing a PCI riser-card assembly for more
information).
- If a voltage regulator has failed, replace the system board.
|
CNFG |
A hardware configuration error has occurred. This
LED is used with the MEM and CPU LEDs.
|
|
CPU |
When only the CPU LED is lit, a microprocessor
has failed.
When the CPU and CNFG LEDs are lit, an invalid microprocessor
configuration has occurred.
|
- Determine whether the CNFG LED is also lit. If the CNFG LED is
not lit, a microprocessor has failed.
- Make sure that the failing microprocessor, which is indicated
by a lit LED on the system board, is installed correctly. See Installing a microprocessor and heat sink for
information about installing a microprocessor.
- If the failure remains, call your next level of support.
- If the CNFG LED is lit, then an invalid microprocessor configuration
has occurred.
- Make sure that the microprocessors are compatible with each other.
They must match in speed and cache size. To compare the microprocessor
information, run the Setup utility and select System Information,
then select System Summary, and then select Processor Details.
- Replace an incompatible microprocessor.
- If the failure remains, call your next level of support.
|
DASD |
A hard disk drive error has occurred. A hard disk
drive has failed or is missing. |
- Check the LEDs on the hard disk drives for the drive with a lit
status LED and reseat the hard disk drive.
- Reseat the hard disk drive backplane.
- For more information, see Resolving hard disk drive problems.
- If the error remains, replace the following components in the
order listed, restarting the server after each:
- Replace the hard disk drive, as described in Removing a hot-swap hard disk drive.
- If the problem remains, call your next level of support.
|
FAN |
A fan has failed, is operating too slowly, or has
been removed. The TEMP LED might also be lit. |
- Reseat the failing fan, which is indicated by a lit LED near the
fan connector on the system board.
- Replace the failing fan, which is indicated by a lit LED near
the fan connector on the system board. See Removing a hot-swap fan for
more information.
Note: If an LED that is next to an unused fan connector
on the system board is lit, a PCI riser-card assembly might be missing;
replace the PCI riser-card assembly. Both PCI riser-card assemblies
must always be present.
|
LINK |
Reserved. |
|
LOG |
An error message has been written to the system-event
log |
Check the system logs for information about the
error. Replace any components that are identified in the error logs. |
MEM |
When only the MEM LED is lit, a memory error
has occurred.
When both the MEM and CNFG LEDs are lit, the
memory configuration is invalid or the PCI Option ROM is out of resource
|
Note: Each time you install or remove a DIMM, you
must disconnect the server from the power source; then, wait 10 seconds
before restarting the server.
- If the MEM LED and the CNFG LED are lit, complete the following
steps:
- Check the system-event log in the Setup utility. If a PCI Option
ROM out-of-resource error log is present, reduce the base system ROM
or change the ROM order.
- Run the DSA memory test to isolate the problem.
- If the test reports that a memory error has occurred, replace
the failing DIMM, which is indicated by the lit DIMM latch on the
system board (the DIMM LED is underneath the DIMM latch).
- If the test reports the memory configuration is invalid, repopulate
the DIMMs to a supported configuration. (See Installing a memory module about memory configuration.)
- If the CNFG LED is not lit, the system might detect a memory error.
Complete the following steps to correct the problem:
- The server did not boot and a failing DIMM LED is lit.
- Reseat the DIMM.
- Run the memory test to isolate the problem.
- If the test indicates that a memory error has occurred (check
the system log), replace the failing DIMM, which is indicated by the
lit DIMM latch on the system board (the DIMM LED is underneath the
DIMM latch).
|
NMI |
A non-maskable interrupt has occurred, or the NMI
button has been pressed. |
Check the system-event log for information about
the error. |
OVER SPEC |
The server was shut down because of a power-supply
overload condition on one of the power channels. The power supplies
are using more power than their maximum rating. |
- If any of the power channel error LEDs (A, B, C, D,
E, or AUX) on the system board are lit also, refer to the section
on "Power problems" in the appropriate server guide in Troubleshooting the System x3650 server. (For
the location of power channel error LEDs, see the section on "Internal
connectors, LEDs, and jumpers".)
- Check the power-supply LEDs for an error indication (AC LED and
DC LED are not both lit, or the information LED is lit). Replace a
failing power supply.
- Remove optional devices from the server.
|
PCI |
An error has occurred on a PCI bus or on the system
board. An additional LED is lit next to a failing PCI slot. |
- Check the LEDs on the PCI slots to identify the component that
is causing the error.
- Check the system-event log for information about the error.
- If you cannot isolate the failing adapter through the LEDs and
the information in the system-event log, remove one adapter at a time
from the failing PCI bus, and restart the server after each adapter
is removed.
- If the failure remains, call your next level of support.
|
PS |
A power supply has failed.
Power supply
1 or 2 has failed.
When both the PS and CNFG LEDs are lit,
the power supply configuration is invalid.
|
- Check the power-supply that has an lit amber LED. (See Table 1 for
more information.)
- Make sure that the power supplies are seated correctly.
- Remove one of the power supplies to isolate the failed power supply.
- Make sure that both power supplies installed in the server are
of the same type.
- Replace the failed power supply.
|
RAID |
Reserved |
|
SP |
The service processor (the IMM) has failed. |
- Remove power from the server; then, reconnect the server to power
and restart the server.
- Update the firmware on the IMM.
- If the failure remains, call your next level of support.
|
TEMP |
The system temperature has exceeded a threshold
level. A failing fan can cause the TEMP LED to be lit. This condition
can also be caused by a room temperature that is too high. |
- Check the error log. If a fan has failed, replace it.
- Make sure that the room temperature is not too high.
- Once you complete the previous steps and feel the
root problem that caused a temperature issue is resolved, the iMM
interface needs to be rebooted to clear the TEMP indicator. Follow
the steps in How to reset/reboot server iMM interface and
then return here.
- If the failure remains, call your next level of support.
|
VRM |
Reserved. |
|