Water specifications for the secondary cooling loop
Learn about the water specifications required for the secondary cooling loop of your heat exchanger.
It is important that the water being supplied to the heat exchanger meet the requirements described in this topic; otherwise, system failures might occur over time, as a result of:
Water control and conditioning for the secondary cooling loop
The water used to fill, refill, and supply the heat exchanger must be particle-free deionized water or particle-free distilled water with appropriate controls for avoiding the following issues.
Because of typical water temperatures (described in Water delivery specifications for secondary loops), the water may not be able to originate from the primary building chilled-water system. Conditioned water for the heat exchanger should be supplied as part of a secondary, closed-loop system.
Important: Use of glycol solutions is not recommended because they can adversely affect the cooling performance of the heat exchanger.
Materials for secondary loops
This topic describes the materials for use in supply lines, connectors, manifolds, pumps, hoses, and any other hardware that makes up the closed-loop water-supply system at your location.
Materials to avoid in secondary loops
Do not use any of the following materials in any part of your water supply system.
Water supply requirements for secondary loops
This topic describes specific characteristics of the system that supplies the chilled conditioned water to the heat exchanger.
Temperature
The heat exchanger, its supply hose and return hoses are not insulated and do not have features designed to address the creation and collection water from condensate. Avoid any condition that could cause condensation. The temperature of the water inside the supply hose, return hose, and the heat exchanger must be kept above the dew point of the location where the heat exchanger is being used.
Attention: Typical primary chilled water is too cold for use in this application because building chilled water can be as cold as 4 - 6 degrees C (39 to 43 degrees F).
Important: If the system supplying the cooling water does not have the ability to measure the room dew point and automatically adjust the water temperature accordingly, the minimum water temperature that must be maintained is 18 degrees C plus or minus 1 degree C(64.4 degrees F plus or minus 1.8 degrees F). This is consistent with the ASHRAE Class 1 Environmental Specification that requires a maximum dew point of 17 degrees C (62.6 degrees F). Refer to the ASHRAE document entitled Thermal Guidelines for Data Processing Environments. Information on obtaining this document is found at www.ashrae.org. Search on document id ASHRAE TC 9.9.
Pressure
The water pressure in the secondary loop must be less than the maximum 689.66 kPa (100 pounds per square inch). Somewhere in the water circuit, a pressure relief valve, set to this maximum value, is required for safety reasons. Normal operating pressure at the rear door heat exchanger should be 137.93 kPa (20 psi) or less.
Flow rate
The flow rate of the water in the system must be in the range of 23 - 38 liters per minute (6 - 10 gallons per minute).
Pressure drop versus flow rate for heat exchangers (including quick-connect couplings) is defined as approximately 48 kPa (7 psi) at 30 liters per minute (8 gallons per minute). Adjustable flow valves are recommended for installation on all supply lines of the water circuit, to enable compliance, to this flow specification.
Water volume limits
The heat exchangers hold between 2.8 liters (0.75 gallons) and 5.3 liters (1.4 gallons). Fifteen meters (50 ft.) of 19 mm (0.75 in.) supply and return hoses hold approximately 9.4 liters (2.5 gallons). To minimize exposure to flooding in the event of leaks, the entire product cooling system (heat exchanger, supply hose and return hose) excluding any reservoir tank should have a maximum 15.1 liters (4 gallons) of water. This is a cautionary statement not a functional requirement. Also consider using leak detection methods on the secondary loop that supplies water to the heat exchanger.
Air exposure
The secondary cooling loop is a closed loop, with no continuous exposure to room air. After you fill the loop, remove all air from the loop. Air bleed valves are provided at the top of each heat exchanger manifold for purging all air from the system.