subscribe iconSubscribe to this information

Model 9406-870 and 9406-890 server specifications

Server specifications provide detailed information for your server, including dimensions, electrical, power, temperature, environment, and service clearances.

This product meets the technical requirements of IEC 61000-3-3.

Models 9406-870 and 9406-890 have some additional information that is important during planning.

model 9406-870 or 9406-890

Pictured is model 9406-870 or 9406-890 server with the 9094 expansion unit

Table 1. Dimensions
Measurements Width Depth Height
Metric (mm) 785 1494 2025
English (in.) 30.91 58.83 79.72
Depth without covers   1173.5 mm (46.2 in)
Standard shipping crate 940 mm (37 in.) 1422 mm (56 in.) 2337 mm (92 in.)
Reduced height shipping crate 940 mm (37 in. 1422 mm (56 in.) 2032 mm (80 in.)
Height reduction feature 0126 System frame is included in two pieces to be fully assembled at customer location.     1.65 m (65 in)
Table 2. Maximum configuration weight
800 kg (1758 lb)
Table 3. Electrical and thermal
Electrical characteristics Properties
kVA (maximum) 8-core (9406-870) 16-core (9406-870) 24-core (9406-890) 32-core (9406-890)

6.315

6.315

8.201

10.099

Rated voltage at 50-60 plus or minus 0.5 Hz (3-phase)3, 4

200-240 V ac

380-415 V ac

480 V ac

Rated current (amperes per phase) 200-240 V ac 380-415 V ac 480 V ac

45 A

25 A

20 A

Thermal output (maximum) 8-core (9406-870) 16-core (9406-870) 24-core (9406-890) 32-core (9406-890)

20.478 kBtu/hr

20.478 kBtu/hr

26.591 kBtu/hr

32.744 kBtu/hr

Power requirements maximum 8-core (9406-870) 16-core (9406-870) 24-core (9406-890) 32-core (9406-890)

6000 W

6000 W

7791 W

9594 W

Power factor 0.95
Frequency (Hertz) 50 to 60
Inrush current3 163 A
Leakage current 42 mA
Phase 3
Table 4. Temperature requirements
Temperature properties Temperature
Operating 10 - 32°C (50 - 89.6°F)
Nonoperating 10 - 43°C (50 - 109.4°F)
Storage 1 - 60°C (33.8 - 140 °F)
Shipping -40 - 60°C (-40 - 140 °F)
Table 5. Environment requirements
Properties Operating Non operating Storage Shipping
Noncondensing humidity 8 - 80% 8 - 100% 5 - 80% 5 - 100%
Wet bulb temperature 23°C (73.4°F) 27°C (80.6°F) 29°C (84.2°F) 29°C (84.2°F)
Maximum altitude 2134 m (7000 ft)      
Table 6. Noise emissions1
  Operating Idle
LWAd 7.2 bels 7.2 bels
LpAm (1-meter bystander) 54 dB 54 dB
Table 7. Service clearances
Front Back Sides 1 Top1
1143 mm 914 mm 762 mm 762 mm
45 in. 36 in. 30 in. 30 in.
Table 8. Notes
Notes:
  1. For a description of noise emission values, see Acoustics.
  2. Inrush currents occur only at initial application of power (very short duration for charging capacitors). No inrush currents occur during the normal power on or off cycle.
  3. The system will function normally with a nominal input voltage in the range of 200-480 V ac, three-phase.
  4. The power supplies automatically accept any voltage with the published rated voltage range. If dual power supplies are installed and operating, the power supplies draw approximately equal current from the utility (mains) and provide approximately equal current to the load.

1Side and top clearances are optional when operating if the building floor loading specifications are met.


Send feedback | Rate this page

Last updated: Tue, June 17, 2014