Pinned topic Enclosure battery conditioning is required but not possible

‏2013-10-11T16:04:35Z |

Hi  

I am  to IBM Storwize V7000. 

During the months, I received an Alert notice from the SAN: # Evetn ID = 045062 Error Code = 1131 : Enclosure battery conditioning required, but not possible # 

Should I be concerned about it?

What caused this alert? 

Many thanks,

Updated on 2013-10-11T16:04:55Z at 2013-10-11T16:04:55Z by LuisJimenez
  • AndersLorensen
    AndersLorensen
    156 Posts

    Re: Enclosure battery conditioning is required but not possible

    ‏2013-10-12T08:25:09Z  

    Yes, you should be concerned! Inside each CPU there is a built in UPS, and these batteries needs to be maintained every 90 days. This happens automaticly, but in your case there is a problem. Might be one PSU is broken, not recieving power or similar.

     

    It could also be related to this maybe? http://www-01.ibm.com/support/docview.wss?uid=ssg1S1004426

     

    --

    Anders

  • chriscanto
    chriscanto
    292 Posts

    Re: Enclosure battery conditioning is required but not possible

    ‏2013-10-13T10:07:05Z  

    Yep, as Anders says, this is something you definitely want to resolve.

    The best starting point is to ensure there are no other unfixed errors in the system event log.  The 1131 error occurs as a side-effect of other problems, rather than being a root cause.

    If in doubt, contact IBM Support.